Iron-loss on three phase transformer
Hello
I just converted the equivalent model of the three phase transformer in Altair 3D to 2D. but i want to compare the core loss and by theory, they should be same or very close. my question is i i set the current in the secondary to be zero how do i get the current to be inputted in the primary side of the three phase transformer so as to simulate no-load condition.
that is the current should be the magnetizing current and phase. how do i get this? is there a method i can use or a way to calculate it ? i attached a picture of the transformer parameters and dimension
Answers
-
Hi Harmony Peter,
Altair Flux 3D has example of Power Transformer, where you can find tests related to Transformers. You can refer to this example, particularly the No-load test to see the specific procedures and setting used in Flux for simulating no-load conditions.
Thank you,
Charishma.0